Forums » Electrical Engineering

Servo motor

    • 27 posts
    March 15, 2019 2:41 PM PDT

    1600VA 400V/230V stepdown transformer feeding my servo motors. Do I need to have the contactor on the input side of the transformer for my  e-stop function to kill power to my servo drives?

    • 3 posts
    March 16, 2019 2:12 AM PDT

    Yes, in some projects it is required to remove the high voltage supplying the servo drive, if there is a stop condition by using opening a contractor.


    This post was edited by Steinberg James at March 16, 2019 2:16 AM PDT