    Is it per code to install a subpanel in a walk in closet?

    • 103 posts
    October 18, 2019 10:44 AM PDT

    240.24(D) Not in Vicinity of Easily Ignitable Material. Overcurrent devices shall not be located in the vicinity of easily ignitable material, such as clothes closets.

    • 157 posts
    October 18, 2019 12:37 PM PDT

    I agree with Steve.  Some people feel that if the panel was installed in a spot where nothing is stored, or out of harms way) then it would permitted.  A situation might be on a wall that the door opens onto.  Most inspectors will not approve it anywhere in the clothes closet